Solved my other issue with the baud settings and had the machine operating in manual mode last night, installed the homing kit this morning and have the following scenario. Enter the $H and the machine homes to the Z axis great and then the x and y start to advance and the x hits the switch and does not back off and the y does not stop and the belt continues to drive. I've checked all connections several times and checked continuity and all's good. Any suggestions ? Thanks Ron
|
|
|
Post by Derek the Admin on Feb 4, 2017 17:57:00 GMT
Hey. I think we can get ya going. Pics are better than text if ya can... but which way are the switches plugged on the board? Sure they aren't crossed? What wire is plugged where on the switches? Do you have continuity from the switch to the controller side of the homing wires?Do you have a good crimp on the wire on the switch side?
|
|
azron
New Member
Posts: 4
|
Post by azron on Feb 4, 2017 18:10:55 GMT
Thanks for the quick reply, just figured out the problem double checked the continuity again and found bad connection on y com connection fixed connection problem solve. Thanks again Ron
|
|